Yes - that is correct. I should have said the circuit breaker on the secondary side should be a ganged double-pole RCBO.
Since both sides of the secondary are +/- 115V with respect to earth, under certain fault conditions there could be a leakage current to earth on one side, but not the other, with the leakage current sufficiently low so as not to trip any safety device on the primary side (such as any fuse in the plug top, or device in the consumer unit).
Yes my thoughts at the time also. Mine is in a metal case though.
“Music has always been a matter of energy to me, a question of fuel. Sentimental people call it inspiration, but what they really mean is fuel. I have always needed fuel. I am a serious consumer. On some nights I still believe that a car with the gas needle on empty can run about fifty more miles if you have the right music very loud on the radio”